Mention four methods of reducing leakage fluxes in a transformer.
ScanSolve AI Answer
This answer stops before the end.
It was cut off when it was first written. Ask ScanSolve this question again for the full working.
Step-by-step solution
5 stepsHere are the solutions to the questions:
QUESTION 1: TRANSFORMERS
1.1: Four methods of reducing leakage fluxes in a transformer are:
- Interleaving of primary and secondary windings.
- Using concentric windings.
- Sectionalizing the windings.
- Using shell-type core construction.
1.2: Given:
Primary voltage
Load resistance
Load reactance
Turns ratio
Equivalent primary resistance
Equivalent primary leakage reactance
Calculate the load impedance referred to the primary side.
The turns ratio .
The load impedance is .
The load impedance referred to the primary is .The total equivalent impedance referred to the primary is .
The magnitude of the total equivalent impedance is:
1.2.1: The primary circulating current ().
The primary current is .The magnitude of the primary circulating current is:
1.2.2: The per unit regulation of the transformer.
The power factor angle is the angle of , so .
The voltage regulation (VR) is given by:The per unit regulation is:
1.2.3: The secondary terminal voltage ().
The voltage across the load referred to the primary is .The secondary terminal voltage is related to by the turns ratio .
The magnitude of the secondary terminal voltage is:
QUESTION 2: MEASUREMENT OF POWER IN THREE PHASE SYSTEMS
2.1: Given:
Line voltage
Frequency
Star connected load
Impedance per phaseCalculate phase voltage, phase current, and power factor.
For a star-connected load, the phase voltage .
The magnitude of the impedance per phase is .
The phase current .
For a star connection, the line current .
The power factor angle .
The power factor .2.1.1: The total power of the load ().
The total power for a three-phase system is .The total power of the load is:
2.1.2: The readings on watt-meters, if two-wattmeter method is used to measure the power taken by the load.
The two wattmeter readings are and .
Here .
The readings on the wattmeters are:
2.2: Calculate the resistance per phase of a three phase , overhead line with solid conductors of diameter, with a symmetrical spacing of between centres. Take resistivity of the conductor material as .
Convert units and calculate the cross-sectional area.
Length .
Diameter , so radius .
Resistivity .
The cross-sectional area .Calculate the resistance per phase.
The resistance is given by the formula .
The resistance per phase is:
QUESTION 3: AC MACHINES
3.1: Given:
Synchronous impedance per phase .
Open circuit line voltage of one alternator .
Circulating current .
Machines are star-connected and in exact phase opposition.Calculate phase values and magnitude of synchronous impedance.
The phase voltage of the first alternator is .
The magnitude of the synchronous impedance is .
3.1.1: The open circuit voltage of the other machine () assuming it is bigger than that of the first machine.
When two alternators are in parallel and in exact phase opposition, the circulating current is given by:This formula assumes and are in phase, and . However, "exact phase opposition" means and are out of phase.
Let and .
The voltage difference driving the circulating current is .
The magnitude of the circulating current is .This result is negative, which contradicts the assumption that is bigger than . This indicates that the problem statement "exact phase opposition" might be interpreted differently in the context of the given circulating current value, or there's an inconsistency in the problem data.
A common scenario for circulating current in parallel alternators is due to a phase difference between EMFs, or a difference in magnitudes when EMFs are in phase. If they are in "exact phase opposition", it usually means they are out of phase.
If the circulating current is where and are phasors, and and , then .
The magnitude of this voltage difference is .
The magnitude of is .
.
This leads to , which is not physically possible for a magnitude.Let's assume "exact phase opposition" means that the resultant voltage causing the circulating current is (phasor difference), and the problem implies that and are in phase but with different magnitudes, and the "phase opposition" refers to the current flow. This is a common source of confusion.
If and are in phase, and , then .
.This value is positive and greater than , consistent with the problem statement.
The open circuit line voltage of the other machine is .The open circuit voltage of the other machine is:
3.1.2: The terminal voltage (line value).
The terminal voltage (phase value) is the voltage at the busbar. It can be calculated using either alternator's EMF and circulating current.
Let'